Life safety elevators

Status
Not open for further replies.

KaYaKe

Member
If I have a 5 story building with an emergency generator and the generator is feeding an emergency panel via an ATS. Can the life safety elevator be fed from the emergency panel OR I should feed it directly from the generator via a second ATS?!

Thanks,

KS
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Typically Elevators are required by the building codes to be connected to standby power not emergency power. You will need to have a separate transfer switch for the standby power.

Contact your locally building department and see what the building code requirements are.

I know that the IBC section 2702.2.5 and 2702.2.19 require that the power for accessible means of egress elevators and standard elevators need to be supplied by standby power.

Chris
 