Lifeline single conductor fire pump cable

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Got a call from a CBO this morning about the above cable bring run through a condo. Just 3 individual cables, no cable tray.


Anyone have any experience with this stuff? Seems to be in violation of 300.3(B) to me.

Thanks
 
Looks similar to Vita Link 2 hour MC cable. Yes you can run three individual cables to make 3 phase feeders. I've had the misfortune of having to install miles of this stuff. Here's an example of single conductor cables that someone else installed. The small box is 3 conductor cable. Yes there are some straps missing.

VitaLink 001.jpg
 
Top