Is an explosionproof seal off required, in the conduit system, from the wet well to the lift station control panel....IF the lift station is installed outdoors and is vented? I have seen drawings & specs from several municipalities. Some jurisdictions require explosionproof seal offs and some do not....if the wet well is vented.
Environment & installation:
Lift station installed outdoors.
Wet well is vented.
Conduit system from control panel to wet well is SCH 80 PVC
Thoughts:
I am thinking this would be a Class 1, Division 2 location [NFPA 70 Ed. 2011 500.5(B)(2)]
On a chart in NFPA 70 2011 Ed. ( 2011 NEC Handbook page 734), the chart title is "Conduit and Cable Sealing Requirements"...Class 1, Division 2..."Conduit run leaving Division 2 location"..."Within 10ft of either side of boundary. No unions, couplings, boxes, or fittings (other than explosionproof reducers) permitted between the seal fitting and the point where the conduit leaves the Division 2 location. Not required to be explosionproof seal."
What does the discussion group think? Please include code references with any response.
Thanks for the help
Environment & installation:
Lift station installed outdoors.
Wet well is vented.
Conduit system from control panel to wet well is SCH 80 PVC
Thoughts:
I am thinking this would be a Class 1, Division 2 location [NFPA 70 Ed. 2011 500.5(B)(2)]
On a chart in NFPA 70 2011 Ed. ( 2011 NEC Handbook page 734), the chart title is "Conduit and Cable Sealing Requirements"...Class 1, Division 2..."Conduit run leaving Division 2 location"..."Within 10ft of either side of boundary. No unions, couplings, boxes, or fittings (other than explosionproof reducers) permitted between the seal fitting and the point where the conduit leaves the Division 2 location. Not required to be explosionproof seal."
What does the discussion group think? Please include code references with any response.