I have commercial car wash facility light is going to be more than three hours operational. Engineer calculated total connected load of branch circuit light in facility to be X fed from panel A. He is saying demand load for panel A is (X)(100%) with 100% demand factor. He is using that calculation to see if the main breaker and bus in the panel board A is not overloaded and to size feeder to panel A.
Two questions:
1. Is their a code section that say connected load has to be multiply by 125% to get light demand load anywhere to see if panel A bus or main breaker is overloaded?
2. Is their a code section that say connected load has to be multiply by 125% to get light demand load for sizing feeder to panel A?