kornbln said:Is this acceptable?
Fluorescent light fixture above shower head. Bottom of the fixture is exactly 8 ft from the bottom of the tub. Fixture is not rated for a damp location.
Dennis Alwon said:It must be at least 8' from the top of the shower threshold not the floor of the shower stall. I say it is not code compliant
Check this outkornbln said:Not sure I understand what you mean... Let me rephrase. It's 8 ft from the bottom of the tub (where the drain is)
nec 410.4 (d) said:(D) Bathtub and Shower Areas. No parts of cord-connected luminaires, chain-, cable-, or cord-suspended luminaires, lighting track, pendants, or ceiling-suspended (paddle) fans shall be located within a zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft) vertically from the top of the bathtub rim or shower stall threshold. This zone is all encompassing and includes the space directly over the tub or shower stall. Luminaires located within the actual outside dimension of the bathtub or shower to a height of 2.5 m (8 ft) vertically from the top of the bathtub rim or shower threshold shall be marked for damp locations, or marked for wet locations where subject to shower spray.
Dennis Alwon said:Stickboy, If it is over the 8' from the threshold of the stall I don't believe it needs to be damp rated.
wireman3736 said:I don't think the 8' is a problem as it doesn't fit in the list of fixtures prohibited, the fact that it is not damp or wet rated would be a problem.
wireman3736 said:the way the original poster put , it is within the 8"
kornbln said:so 8ft 1in would be ok?
Dennis Alwon said:The odd thing is if it were a tub it would have to be 8' from the tub rim. How this affects the damp location rating is beyond me.
8' above the shower rim is about 8' 4" above the floor. 8' above the tub rim is about 10' off the floor.
I am guessing there are two things going on here. The ability to reach the fixture from the shower & tub and the damp rating. Seems like something is amiss.