mshields
Senior Member
- Location
- Boston, MA
We've got a problem with lights flickering in an MRI room when the MRI is ramped up; i.e. when a patient is being scanned. The lights are designed for the application, the conduit with all power and signal is shielded with the exception of a 24V circuit which actually uses PVC. NOW, this is I'm requiring to be changed out as it is a) not in accordance with our spec, b) the lighting manufacturer's recommendations and while it has no bearing on the flicker issue it happens to be not in conformance with NEC 517.13 requiring redundant grounding inclusive of metallic conduit to patient care area's.
The cost of changing out this conduit is going to be substantial insofar as they need to shut down the magnet; apparently a very expensive proposition. The aggravation of the client is even more severe.
My concern, is that the PVC conduit was actually installed as per the MRI manufacturer's service tech who is stating that he's seen it done this way in countless applications and is sure it's not the problem. My thought is to first try wrapping the conduit in copper tape, so as to test the notion that the PVC conduit is in fact the culprit.
Bearing in mind that armed with this same copper tape, the contractor has plugged up all other potential sources of leakage, my question is; is there anything else any of you would recommend our doing to diagnose this problem.
Thanks,
Mike
The cost of changing out this conduit is going to be substantial insofar as they need to shut down the magnet; apparently a very expensive proposition. The aggravation of the client is even more severe.
My concern, is that the PVC conduit was actually installed as per the MRI manufacturer's service tech who is stating that he's seen it done this way in countless applications and is sure it's not the problem. My thought is to first try wrapping the conduit in copper tape, so as to test the notion that the PVC conduit is in fact the culprit.