Light Pole Receptacle

Merry Christmas

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Have a job that is being bid in the design stage(not fully designed). There are a lot of light pole with a receptacle on them. They said to figure two conduits to the light pole. One for the light and one for the receptacle. Is that a bad design? I understand if they come from different panels then they may need to be feed from separate conduits.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Separate conduit would be specified for the GC's laborers, to prevent 277v convenience receptacles.

Nobody awards bids to EC's, until permits are held up without them..
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
One for the light and one for the receptacle. Is that a bad design?
No it's not a bad design but it will obviously cost more than running a single conduit. If that's what they want and they're paying for two conduits then that's what you give them. More money for you.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Separate conduit reduces errors between different Nominal Voltage Systems, per 215.12(C)(1)
 