light pole rounding

Status
Not open for further replies.

101010

Senior Member
Installed a 20 foot light pole . It has a egc from the panel. Didnt see a bonding lug for the pole only the ground from the fixtures. Is this ok to ground the pole through the fixture ? or do you have also physically bond the pole?
 
stickboy1375 said:
Does a grounding screw actually have to be green?

Sometimes...but not this time ;)

I find a 1/4 - 20 or larger bolt works better for this application.
 
celtic said:
NEVER is such a powerful word...so final.

Is that your final answer?

You're right I should have said "almost never". If you choose to use a screw as a main bonding jumper or a system bonding jumper than it is required to be green. Although it doesn't have to be a screw.
 