light poles and rec.

Status
Not open for further replies.

crice

Member
Can the conductors feeding 277v lights, and 120V rec. on pole lights be run in the same conduit, considering both ORIGINATE from seperate services? Common sense would say no, but I can find nothing in the code preventing it.
'preciate the help,
Carl
 

480sparky

Senior Member
Location
Iowegia
Most building wire is rated 600v, so yes, they can be in the same raceway. Just use a completely different color scheme for each system.
 