Here is one to chomp on after you finish your Turkey,
an interesting service call yesterday;
After replacement of 400W MH with LED a few Parking lot lights were dim and in different patterns each time the contactor was engaged.
After many hours of swapping lights, getting new lights and who knows how much troubleshooting we get called in to help.
The lighting contractor did not change any wiring at the pole bases.
There are two wires that go up each pole to the light heads so there is no chance the lighting contractor messed up anything.
I found two groups of two poles to be wired in series!
That is light pole 1 and 2 connected in parallel and pole 3 and 4 connected in parallel, however the two groups were connected in series to a two wire 208V supply (off a 208Y120 panel).
The connections were old and obviously unchanged from many decades ago.
How could this have worked fine for decades?
an interesting service call yesterday;
After replacement of 400W MH with LED a few Parking lot lights were dim and in different patterns each time the contactor was engaged.
After many hours of swapping lights, getting new lights and who knows how much troubleshooting we get called in to help.
The lighting contractor did not change any wiring at the pole bases.
There are two wires that go up each pole to the light heads so there is no chance the lighting contractor messed up anything.
I found two groups of two poles to be wired in series!
That is light pole 1 and 2 connected in parallel and pole 3 and 4 connected in parallel, however the two groups were connected in series to a two wire 208V supply (off a 208Y120 panel).
The connections were old and obviously unchanged from many decades ago.
How could this have worked fine for decades?