Not that I've ever known.
I've only wired residential elevators, a couple dozen of them. But here's what I go by, with no mention of water or pilot lighted switch...
620.24 Branch Circuit for Hoistway Pit Lighting and Receptacle(s).
(A) Separate Branch Circuit. A separate branch circuit shall supply the hoistway pit lighting and receptacle(s).
Required lighting shall not be connected to the load side of a ground-fault circuit interrupter.
(B) Lighting Switch. The lighting switch shall be so located as to be readily accessible from the pit access door.
(C) Duplex Receptacle. At least one 125-volt, single-phase, 15- or 20-ampere duplex receptacle shall be provided in the hoistway pit.
Informational Note: See ASME A17.1-2010/CSA B44-10, Safety Code for Elevators and Escalators, for illumination levels