Jody Boehs
Member
- Location
- Fairview, Oklahoma, USA
- Occupation
- Controls and Electrical Manager
Hi,
My company is building a 380' x 320' warehouse. I have attached a photo of our lighting layout. My plan is to put each Bay of lighting on its own 20A circuit. 15 bays total. Each bay has 6-9 lights. The lights being installed are 240W 277V LED UFO fixtures. If my calculations are correct, each bay will pull around 8 amps assuming all lights are ON. Some of the lights will be on motion sensors. My question, however, is this.... I have always been told to increase the size of wire for each 100' of length to minimize voltage drop. The panels for this building will be on the left side and center of the attached image. If I am using 20A circuits (12 awg wire), that would mean I would have to use 6 awg wire to reach all the way across the building. There's got to be a better way to do this. Any ideas?
My company is building a 380' x 320' warehouse. I have attached a photo of our lighting layout. My plan is to put each Bay of lighting on its own 20A circuit. 15 bays total. Each bay has 6-9 lights. The lights being installed are 240W 277V LED UFO fixtures. If my calculations are correct, each bay will pull around 8 amps assuming all lights are ON. Some of the lights will be on motion sensors. My question, however, is this.... I have always been told to increase the size of wire for each 100' of length to minimize voltage drop. The panels for this building will be on the left side and center of the attached image. If I am using 20A circuits (12 awg wire), that would mean I would have to use 6 awg wire to reach all the way across the building. There's got to be a better way to do this. Any ideas?