I did a search prior to starting this thread and didn't come up with anything, but it could have been discussed before.
I am inclined not to treat 99% of lighting loads as continuous when calculating today. In a typical office in Florida, occupancy sensors are required throughout which means lights will not remain on for more than 3 hours continuously in most cases. Secondly, unless you are using 220.12 Exception No. 1 (and likely even then) the actual lighting load is going to be less than the lighting load per table 220.12. I would contend that you could apply the continuous load factor prior to comparing your load to table 220.12. So, if your LED load less than 80% of the table load, then it is still under the table load and the va per foot per table 220.12 could be used without applying the load factor.
What do you think?
I am inclined not to treat 99% of lighting loads as continuous when calculating today. In a typical office in Florida, occupancy sensors are required throughout which means lights will not remain on for more than 3 hours continuously in most cases. Secondly, unless you are using 220.12 Exception No. 1 (and likely even then) the actual lighting load is going to be less than the lighting load per table 220.12. I would contend that you could apply the continuous load factor prior to comparing your load to table 220.12. So, if your LED load less than 80% of the table load, then it is still under the table load and the va per foot per table 220.12 could be used without applying the load factor.