Does it state in the NEC that lighting loads are continuous? Is it just our knowledge that the circuits we are considering a calculation for are continuous? I was always taught to never load a lighting circuit to more than 80 %. Thank you, Trent
No it does not.
Lighting loads can be either continuous or not.
For instance the sales floor lighting in a store would be considered continuous. On the other hand a closet light would not be.
The determining factor is found in article 100.
Continuous Load. A load where the maximum current is expected to continue for 3 hours or more.