Lighting Calc

Merry Christmas

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Hello. I have a 120/208v distribution center. I have these ttwo fixture type that are site lights. What calcution would I use to determine circuit size? Also VD would be an issue as they are 500 to 800' away from source. I'm think I can use 20A breaker(s) but would need ot upsize wire then tap it down at panel and when I branch off to fixtures. Does that make sense?

1728474479732.png
1728474394862.png
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How many lights on a circuit? You could put 72 on a single 20 amp circuit. 1800 Watt/25=72
 

Ragin Cajun

Senior Member
Location
Upstate S.C.
Careful with voltage drop. Bollards can stretch way out there.
Also, too many LED fixtures can cause false trips. Don't ask how I know. I just don't know the cut off number.
And when using dimmers, you are severely restricted in the load with LED's
RC
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
You started off by saying you have a 120/208 distribution system.
Yes but it's not designed so I just figured. But it would be better to distribute the power to the poles at 277v( since it's very long distances) I'd think even if I need to put transformer by service.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
GM. Just so I'm clear the 1,800W values comes from where?
Continuous load no more than 80% of the branch circuit rating. You started out by saying in the OP 120/208 volts so I can see the confusion because you later stated 277 volts. In my original example I used 120 volts. {20 amps*120 volts*80%=1800 watts} The value will change based on the circuit voltage.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Continuous load no more than 80% of the branch circuit rating. You started out by saying in the OP 120/208 volts so I can see the confusion because you later stated 277 volts. In my original example I used 120 volts. {20 amps*120 volts*80%=1800 watts} The value will change based on the circuit voltage.
1800W is for 277/480. What's the wattage for 120/208v?
 