Lighting Calc

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Hello. I have a 120/208v distribution center. I have these ttwo fixture type that are site lights. What calcution would I use to determine circuit size? Also VD would be an issue as they are 500 to 800' away from source. I'm think I can use 20A breaker(s) but would need ot upsize wire then tap it down at panel and when I branch off to fixtures. Does that make sense?

1728474479732.png
1728474394862.png
 
How many lights on a circuit? You could put 72 on a single 20 amp circuit. 1800 Watt/25=72
 
Careful with voltage drop. Bollards can stretch way out there.
Also, too many LED fixtures can cause false trips. Don't ask how I know. I just don't know the cut off number.
And when using dimmers, you are severely restricted in the load with LED's
RC
 
You started off by saying you have a 120/208 distribution system.
Yes but it's not designed so I just figured. But it would be better to distribute the power to the poles at 277v( since it's very long distances) I'd think even if I need to put transformer by service.
 
GM. Just so I'm clear the 1,800W values comes from where?
Continuous load no more than 80% of the branch circuit rating. You started out by saying in the OP 120/208 volts so I can see the confusion because you later stated 277 volts. In my original example I used 120 volts. {20 amps*120 volts*80%=1800 watts} The value will change based on the circuit voltage.
 
Continuous load no more than 80% of the branch circuit rating. You started out by saying in the OP 120/208 volts so I can see the confusion because you later stated 277 volts. In my original example I used 120 volts. {20 amps*120 volts*80%=1800 watts} The value will change based on the circuit voltage.
1800W is for 277/480. What's the wattage for 120/208v?
 