eplanajr
- Washington
- Project Manager - Utility
Several switches are suddenly tripping the breaker.
15A Homeline AFCI breaker feeding 15 switches. I built the home 18 months ago. Was working fine throughout the day. Went upstairs to put kids to bed and suddenly a trip.
Any ideas?
- 12 of the 15 switches will trip the breaker.
- The switches control (50) LED specific light fixtures at 8W - 9W each, and (4) bathroom fart fans.
- All switches have been checked. No issues with wiring found with wiring. No neutrals shared with any other circuits.
- (1) Timer switch was replaced with regular 1P switch as part of trouble shooting.
- AFCI breaker was swapped for a known good breaker (AFCI) same result.
- AFCI breaker was swapped for a regular breaker - breaker holds (obviously because it doesn't trip because it isn't a GFCI either.
- The Square D, smart diagnostic tool on the breaker indicates a ground-fault. None of the wiring in the boxes looks like it is touching.
- In process of checking every single light fixture to ensure there aren't any wiring issues, more than halfway done. So far so good.
Any ideas?