Is there any minimum clearance above the ground for an overhead branch circuit conductor? I am running Type TC cable attached to a messenger cable between light light poles. Thank you for your assistance.
Scott
charlie
Indianapolis
Re: Lighting Conductor Height above Ground
Assuming this is an Article 225 issue, find the appropriate location and then apply Section 225.18.
(1) 3.0 m (10 ft) - above finished grade, sidewalks, or from any platform or projection from which they might be reached where the voltage does not exceed 150 volts to ground and accessible to pedestrians only
(2) 3.7 m (12 ft) - over residential property and driveways, and those commercial areas not subject to truck traffic where the voltage does not exceed 300 volts to ground
(3) 4.5 m (15 ft) - for those areas listed in the 3.7-m (12-ft) classification where the voltage exceeds 300 volts to ground
(4) 5.5 m (18 ft) - over public streets, alleys, roads, parking areas subject to truck traffic, driveways on other than residential property, and other land traversed by vehicles, such as cultivated, grazing, forest, and orchard