hello I have 6- 20 amp 240 volt LED lighting circuits and i need them all to be controlled by 1 timer. I am unfamiliar with what kind of contactor i need any info is appreciated
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
A lighting contactor is merely a relay with many poles. You need to switch 12 lines. (For 240v loads, you don't "have" to switch both lines, bu tit's still a good idea.) A 12-pole lighting contactor costs way, way more than either three 4-pole contactors or four 3-pole contactors.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Have a panel shop make you a control panel, it will faster a d better than you can make . Put a HOA switch in the door a a pilot light. An hour meter would be useful.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might also need to take the location of the contactors in mind. Electicall held contactors can make a little noise when in operation. Often not a problem, but in some cases unacceptable. Mecanically held contactors will not make noise once energized but the contactors are more expensive
 