You are constructing an Industrial Control Panel since it has more than one power/control circuit, so in order for it to be considered listed, a UL panel shop would need to build it (or I believe field inspect it).
What if the control circuit is tapped from the power of the controlled circuit?You are constructing an Industrial Control Panel since it has more than one power/control circuit, so in order for it to be considered listed, a UL panel shop would need to build it (or I believe field inspect it).
''Assembly''was the word I was look for when I was writing my post. The GC has a 200a 3 pole contactor 120v coil mounted inside a 22'' x 38'' nema 4 enclosure. The enclosure takes up most of the space and takes up and area I need to place my equipment. I asked GC if I could purchase a smaller enclosure to install the contactor and he mentioned it wouldnt be UL listed. I asked him what made his box listed for contactor and he couldnt answer. So it made me think what makes this ''Assembly'' UL list? I have UL listed parts so why cant my Assembly be UL listed.While the "assembly" may not be listed, I wouldn't let that stop me.
I'm not sure it needs to be.I have UL listed parts so why cant my Assembly be UL listed.
If you are a UL 508A panel shop it can be listed. I don't personally see why it needs to be but if UL listing of the assembly is a requirement that is pretty much how it's going to have to be.''Assembly''was the word I was look for when I was writing my post. The GC has a 200a 3 pole contactor 120v coil mounted inside a 22'' x 38'' nema 4 enclosure. The enclosure takes up most of the space and takes up and area I need to place my equipment. I asked GC if I could purchase a smaller enclosure to install the contactor and he mentioned it wouldnt be UL listed. I asked him what made his box listed for contactor and he couldnt answer. So it made me think what makes this ''Assembly'' UL list? I have UL listed parts so why cant my Assembly be UL listed.
An "Industrial Control Panel" is defined as an assembly of two or more components.''Assembly''was the word I was look for when I was writing my post. The GC has a 200a 3 pole contactor 120v coil mounted inside a 22'' x 38'' nema 4 enclosure. The enclosure takes up most of the space and takes up and area I need to place my equipment. I asked GC if I could purchase a smaller enclosure to install the contactor and he mentioned it wouldnt be UL listed. I asked him what made his box listed for contactor and he couldnt answer. So it made me think what makes this ''Assembly'' UL list? I have UL listed parts so why cant my Assembly be UL listed.
You can have a Listed open style contactor and you can have a listed ENCLOSED contactor if listed by the manufactu8rer that way. But if you buy a listed open style contactor and put it in your own enclosure, that becomes an "Industrial Control Panel" that needs to be listed as such, because there are rules about enclosure size, wire bending space requirements, heat rise, short circuit current ratings, labeling etc. that must be followed. When the manufacturer puts together and sells an "enclosed" lighting contactor, they had to go through that process separately for the enclosed version even though the open version was already listed. Everyone must follow those rules.1.3 This equipment consists of assemblies of two or more components, such as motor controllers,
overload relays, fused disconnect switches, circuit breakers, and related control devices such as
pushbuttons, pilot lights, selector switches, timers, control relays, and similar devices, with associated
wiring, terminal blocks, and similar components.
What about using an empty enclosure made for contactors, and putting one in it?
View attachment 2558925
Is that as good as getting one with a contactor already in it?
View attachment 2558926
Is what appears to be putting a contactor in a generic contactor enclosure okay?
View attachment 2558927
But doing it this way is out of the question?
View attachment 2558928
I'm glad. I thought I was just asking it more clearly.Thanks for reply you answered question perfect.
There is nothing wrong with it. UL has convinced the world that unless it's been blessed by their overlords, the world will burn to the ground. I've seen more than a few UL-stickered panels that came out of UL508A shops that were an absolute nightmare. Somehow, that was OK because the magic sticker make everything OK, but an electrician field installing a contactor in an enclosure is "bad." <rant/>I've purchased Hoffman boxes that have removable backplates for many jobs. I've never had an inspector question the validity or listing of any devices that I installed on the backplate. I've even put a 3pole 30A definite purpose contactor in an 8 x 8 screw cover J box to use a master switch to turn all the lights in a home before. May be wrong but I don't see any problem with it.