John it may be a design decision but when switching emergency lighting Article 700 pushes us to using NC contactors.Originally posted by john m. caloggero:
The NEC does not require either NO or NC contacts for lighting control contactors. This is design consideration.
How do you wire the control circuit for these? I've always wondered, but never had a chance to play with one.Originally posted by infinity:
We prefer mechanically held lighting contactors. The coil is only energized while it is changing from open to closed and vice versa.
Basically they have a coil that moves when it's energized. If you energize the common(L) and close(C) terminals the relay will latch in the 'on' position. There is a aux switch in series with both the open and close positions that stop power from reaching the coil once that position has been energized. This keeps the coil energized only for a fraction of a second.How do you wire the control circuit for these? I've always wondered, but never had a chance to play with one.
I have heard of installations such as this. However I would think that this would violate 700.3 unless that relays were approved for use on emergency systems.I just had to wire up several rooms where the emergency light fixture was switched with the rest of the fixtures in the room, but when power went out, the X fixtures had to come on. For this setup, I used 2 RIB relays in each room. One coil was activated by the switch leg power to switch the X power. The other was powered by the constant normal power to switch the X power through the NC contacts when a power loss was detected.
700.3 Equipment Approval.
All equipment shall be approved for use on emergency systems.
That's what I was wondering. So traveller "A" would be the "on" coil, and the "B" traveller would be the "off" coil. That's just cool.Originally posted by infinity:
Also, these contactors can be controlled from one location with a simple 3-way switch....
That is interesting. I'll have to check the RIB's and see. I know for a fact that the inspector won't check it, but I'd like to find out for myself. We were wondering why the EE designed it this way in the first place. One lamp in a 2x2 3-lamp trouffer is on the X panel in each room. I would have just left them on 24/7. We're not talking a big savings in power by switching them.Originally posted by infinity:
I have heard of installations such as this. However I would think that this would violate 700.3 unless that relays were approved for use on emergency systems.I just had to wire up several rooms where the emergency light fixture was switched with the rest of the fixtures in the room, but when power went out, the X fixtures had to come on. For this setup, I used 2 RIB relays in each room. One coil was activated by the switch leg power to switch the X power. The other was powered by the constant normal power to switch the X power through the NC contacts when a power loss was detected.
700.3 Equipment Approval.
All equipment shall be approved for use on emergency systems.
The system already in place is a generator backup with transfer switch to the required 700 system. The EM ballasts you mention are battery backup and the EE did not spec those. He has on other jobs I've done under him, but those jobs did not have to have article 700 emergency systems.Originally posted by benaround:
Paul,
They make EM ballasts just for this application,you need to run a constant hot to EM ,it will switch on/off unless the constant power goes out which will activate EM ballast.