Lighting Control : Site Lighting Relay Panel

Status
Not open for further replies.
Hi,

Im busy doing the lighting for a site, I have about 3 light circuits (347V,20A) that need to be controlled, i.e they must be connected to a photocell and timer/timeswitch.

Im not sure how the wiring will work, would I need just one relay panel with 3 relays connected to one timeswitch and photocell or would I need three separate photocells and timeswitches?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If you want them all to behave the same (turn on, off at the same time), one photocell and time switch will suffice.
 