Lighting controller, e-lights and exit lights

Status
Not open for further replies.
Location
San francisco bay area
Occupation
Inspector
Hoping someone can help me out. so we have lighting circuits, e-lighting and exit signage in different conduits but all terminating into one 12x12 junction can and then connecting to the relays. please see picture below. also dont mind the complete mess this guy left us. Any advice would be greatly appreciated. I do understand 700.10 but looking for other opinion.

https://photos.google.com/album/AF1.../AF1QipNFX6enXoTUHuU6CdCy97txecPv6VljzqOGzokU
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If they are actually Article 700 circuits, they cannot be in the same raceway or enclosure with any non-emergency circuit. There are no options.
 