I'm having a debate with a colleague about the need to multiply the actual lighting load of a circuit by 125% when calculating the demand kVA of a panel. For example, if there are (10) 293W LED fixture on a circuit, the actual load of that circuit is 2,930VA (assume pf=1). My friend is saying that total needs to be multiplied by a load factor of 1.25 for lighting being a continuous load when calculating the load on the panel. My understanding is the 125% factor is only for determining the overcurrent protection and branch wiring size of THAT circuit, but the actual connected load (demand factor =1) is what is used to determine the load on the panel.
So who is correct? is the panel load = 2,930VA or =3,663VA?