maggmick

Member
Is their any requirement for supporting lighting fixtures from building structure independantly from suspended ceiling other than engineers specifications?
 
Re: Lighting Fixture Support

410.16
(C) Suspended Ceilings. Framing members of suspended ceiling systems used to support luminaires (fixtures) shall be securely fastened to each other and shall be securely attached to the building structure at appropriate intervals.
Luminaires (fixtures) shall be securely fastened to the ceiling framing member by mechanical means such as bolts, screws, or rivets. Listed clips identified for use with the type of ceiling framing member(s) and luminaire(s) [fixture(s)] shall also be permitted.
 
Re: Lighting Fixture Support

Thanks for your reply, but the code does not say that the fixture must be supported independently from the suspended ceiling to the structure. If there is a code for this please let me know.
 
Re: Lighting Fixture Support

Originally posted by maggmick:
Thanks for your reply, but the code does not say that the fixture must be supported independently from the suspended ceiling to the structure. If there is a code for this please let me know.
You will find those requirements in your state's building code.
 
Re: Lighting Fixture Support

Here is a couple places you can look.
Light Fixture Support From Ceiling Wires (Independent Of The Ceiling Support Wires) Opposite Corners Of Light Fixture (2000 IBC 1621.2.5) {1997 UBC section 25.213}
-Ed
 
Re: Lighting Fixture Support

Ma$$achu$ett$ building code requires that any light fixture with a ballast must have 2 support wires or chains that will support the fixture in case the firs department deliberately pulls down the suspended ceiling.

On my jobs here in Ohio I do this anyways as solid steel wire is pretty cheap. One time when I was installing 24 inch diameter ductwork above the suspended ceiling in a hallway the fluorescent fixture fell down right behind my head. I had the suspended ceiling partly dismantled to get a big stepladder up there and the ceiling was not as stable as I thought it was.

This is just not a building code requirement - the law of gravity requires it particularly when doing other work.

One time I was building a 12 foot by 12 foot triangular suspended ceiling and had to install sheet metal screws where the main tees and cross tees ended at the wall. There was no other way to make a grid that small to be structurally stable.
 