F faresos Senior Member Feb 23, 2013 #1 Per the NEC, the room housing emergency equipment such as inverter system for lighting does not need to be located in 2-hrs fire rated room if the building is sprinkled. Is there any other codes will require the room to be fire rated? Thanks,
Per the NEC, the room housing emergency equipment such as inverter system for lighting does not need to be located in 2-hrs fire rated room if the building is sprinkled. Is there any other codes will require the room to be fire rated? Thanks,
iwire Moderator Staff member Location Massachusetts Feb 25, 2013 #2 You don't show a location but in Massachusetts it has to be in a rated room seperate from the normal power panels and equipment.
You don't show a location but in Massachusetts it has to be in a rated room seperate from the normal power panels and equipment.
F faresos Senior Member Feb 25, 2013 #3 iwire said: You don't show a location but in Massachusetts it has to be in a rated room seperate from the normal power panels and equipment. Click to expand... Its in Kansas and we do have it in a dedicated room but not sure if it needs to be fire rated. This building is a two stories building. Thanks,
iwire said: You don't show a location but in Massachusetts it has to be in a rated room seperate from the normal power panels and equipment. Click to expand... Its in Kansas and we do have it in a dedicated room but not sure if it needs to be fire rated. This building is a two stories building. Thanks,