Small job; gas station with convenience store; 800Amp, 120/208V, 3-phase service. There is a 125VA lighting inverter on the job for emergency egress lighting. Can this inverter also serve CO2 monitor? The CO2 monitor fits into the 125VA load-wise; does the load type matter here, the fact that the CO2 monitor is not lighting load? Thank you!
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
The first thought that popped into my head is why would you need to. I would think that if there is a power failure everybody needs to leave the store. Also, doesn't the monitor have its own battery backup?

-Hal
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
The first thought that popped into my head is why would you need to. I would think that if there is a power failure everybody needs to leave the store. Also, doesn't the monitor have its own battery backup?

-Hal

I can’t imagine it would not have a battery backup.

Shouldn’t be any reason to connect to inverter. Is this a cord & plug CO monitor? I’d be worried about someone plugging something else into the receptacle after the job is done and blowing the inverter fuse.


Sent from my iPhone using Tapatalk
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
A lighting inverter used for Artical 700 emergency lighting can not supply any other loads. Also likely a violation of the UL 924 listing for emergency lighting equipment.
 
Last edited:

curious101

Senior Member
Location
Atlanta, GA, USA
The first thought that popped into my head is why would you need to. I would think that if there is a power failure everybody needs to leave the store. Also, doesn't the monitor have its own battery backup?

-Hal
Thanks for responding! The monitor doesn't have its own battery backup.
 

curious101

Senior Member
Location
Atlanta, GA, USA
I can’t imagine it would not have a battery backup.

Shouldn’t be any reason to connect to inverter. Is this a cord & plug CO monitor? I’d be worried about someone plugging something else into the receptacle after the job is done and blowing the inverter fuse.