Matt Mckenzie
Member
- Location
- United States
If you have a 400kw 277v lighting load operating at continuous duty what is the minimum over current device that can be used? 400,000 va x 125% = 500,000va/(480x1.732)= 601.4 amps. Minimum size OCP 700amps correct?