lighting load please help

Status
Not open for further replies.
If you have a 400kw 277v lighting load operating at continuous duty what is the minimum over current device that can be used? 400,000 va x 125% = 500,000va/(480x1.732)= 601.4 amps. Minimum size OCP 700amps correct?
 
Status