Lighting outlet Box

Status
Not open for further replies.

dafixa

New member
Location
Maryland
What is the Code for installing an out let box for a bath room light fixture? Do you have to have a box for the wire connections to fit into or is it okay for the wire to be connected inside the fixture? (New home construction)
 

bphgravity

Senior Member
Location
Florida
Re: Lighting outlet Box

Generally speaking, all connections, junctions, and splices should take place within a box. However, some fixtures are listed as use with space allowances for fixture lead connections to branch-circuit wiring. Some fixtures are listed as raceways as well. See Section III of Article 410 including 410.31 and 410.32 for additional box/fixture requirements. Aslo see Article 310.15(J).
 
A

a.wayne3@verizon.net

Guest
Re: Lighting outlet Box

Simply put,if there is a canopy then there meust be a box !!!!!!!!! I f tit is a vanity strip then all that you need is a stub on rough in and a connector on trim out.
 