Lighting outlet required?

NTesla76

Senior Member
Location
IA
Occupation
Electrics
Per 210.70(C), a lighting outlet is required in attics for equipment requiring servicing. My question is, is a lighting outlet required for a cord and plug radon fan?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Reluctantly, I am of a different opinion than Hal.
To me the fan is likely to require servicing thus a light is needed.
 

NTesla76

Senior Member
Location
IA
Occupation
Electrics
I could actually go either way on it. Would replacing the fan motor be considered servicing? Curious as to the reason behind the yes or no opinions.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I read some of the fan brochures and it appeared they required occasional servicing.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Would a sump pump require a light? Laundry tray pump?
In most instances, why wouldn't the existing illumination suffice or be made to suffice?
Don't service people carry drop lights or other portable lighting?

-Hal
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Would a sump pump require a light? Laundry tray pump?
In most instances, why wouldn't the existing illumination suffice or be made to suffice?
Don't service people carry drop lights or other portable lighting?

-Hal
If there is existing illumination for the area where the equipment is located, there is no requirement to provide an additional lighting outlet.

No idea of how you would use a laundry tray without existing illumination.
 