lighting over swimming pools
efiefi
New member
can some give the requirment for lighting over a pool on gfi, do you still have to be five ft from pool wall
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
If indoor read art 680.22(B)(2)
(2) Indoor Clearances. For installations in indoor pool areas, the clearances shall be the same as for outdoor areas unless modified as provided in this paragraph. If the branch circuit supplying the equipment is protected by a ground-fault circuit interrupter, the following equipment shall be permitted at a height not less than 2.3 m (7 ft 6 in.) above the maximum pool water level:
(1) Totally enclosed luminaires
(2) Ceiling-suspended (paddle) fans identified for use beneath ceiling structures such as provided on porches or patios