Lighting panel addition

Status
Not open for further replies.

shawn73

Member
Location
Napoleon, Ohio
I have a 480V lighting panel with a single conduit run coming out to a junction box, branching off to my lights. I need to add more circuits. I am adding an additional 480V panel next to the existing one. Is it legal for me to bring my remaining light circuits out of the new panel, into the other panel and out through the single conduit run to my junction box? Thanks.
 
Re: Lighting panel addition

Maybe.

You must meet the requirements of 312.8 in order to use a cabinet containing a panelboard as a raceway.
 