I have a SQD, 42 cicuit, 225A,MB lighting panelboard feeding a second SQD, 42 circuit, 225A, MLO panelboard. It is a parallel feed to the second panelboard from the first. The panelboards have two 2.5"x12" EMT conduit connecting the two. One of these is used for the feeders going to the second panelboard.
The MB panelboard has a 4-wire system with grounding electrode conductor. The second panelboard only has a 4-wire with no grounding electrode, equipment grounding conductor, or bonding conductor from the first panelboard.
My question is that I believe this second panelboard is not a sub-panel, merely an extension of the first panelboard providing 84 circuits for lighting and appliances. I also believe that the grounding electrode conductor needs to be taken to the second panleboard and that the raceway should be bonded on both sides with a bonding locknut.
My problem is that if this is all true, I cannot find the code that relates to this if it has to be done or not.
Any help would be greatly appreciated.
The MB panelboard has a 4-wire system with grounding electrode conductor. The second panelboard only has a 4-wire with no grounding electrode, equipment grounding conductor, or bonding conductor from the first panelboard.
My question is that I believe this second panelboard is not a sub-panel, merely an extension of the first panelboard providing 84 circuits for lighting and appliances. I also believe that the grounding electrode conductor needs to be taken to the second panleboard and that the raceway should be bonded on both sides with a bonding locknut.