I will be installing new lighting in an industrial setting.
Ceiling is greater than 20 feet.
fixtures are 4lamp and 6lamp T-8's.
I am being asked to use 16/4 SEOOW cord as fixture whips from the J-box to the fixture. I am not finding in the code where I can verify that 16/4 is sufficient ampacity for this installation.
Art. 400.7 states that flexible cord can be used for the wiring of luminaires. 400.5 states the allowable ampacityas 10A to 13A.
We will be utilizing 3 wire SEOOW ( one hot and a nuet with Gnd.)
What is the max allowable length of the SEOOW as a fixture whip?
Is 16/4 sufficient?
All lighting is 277V and will be controlled by a 20A breaker / motion sensors