Re: Lighting Study
If you measure 20A on each of the three phases
for phase A 277*20=5540W
for phase B 277*20=5540W
for phase C 277*20=5540W
totaling 16,620W
The other method is 480*20*sqrt(3)= 16,627W which is the same if you consider the rounding of the sqrt(3) is off slightly.
So, same answer either way.