Hi,
I have a 112.5 kVA transformer which is 600' away of my switchgear. The actual load that is fed by this transformer is 80 kVA. My question is how should I calculate the voltage drop to size the primary cable?
If I condsier the actual load and 2% voltage drop then I can size a 4/0 cable for primary, but if I consider 112.5 kVA as a load then I need to select the a 350Kmil cable for 2% voltage drop.
What do you think which one make more sense?