infinity said:I would disagree that you can enter a Bilco door. These doors are designed to be locked with a bolt style lock on the inside only. They can not be opened from the outside.
I disagree (always happy to do that! :lol: :lol: )iwire said:infinity said:I would disagree that you can enter a Bilco door. These doors are designed to be locked with a bolt style lock on the inside only. They can not be opened from the outside.
As the owner of one of these doors I agree. 8)
I will admit that the only reason I knew that is from having read another thread in the Forum. That thread asked if it was OK for a main panel to be in a basement area that could only be accessed from the outside, via a bilco door.Optional keyed exterior lock kit available.
charlie b said:I disagree (always happy to do that! :lol: :lol: )
infinity said:I would disagree that you can enter a Bilco door. These doors are designed to be locked with a bolt style lock on the inside only. They can not be opened from the outside.
Even if it is only an exit, then it still requires an outdoor lighting outlet.210.70(A)(2)(b) For dwelling units, attached garages, and detached garages with electric power, at least one wall switch?controlled lighting outlet shall be installed to provide illumination on the exterior side of outdoor entrances or exits with grade level access. A vehicle door in a garage shall not be considered as an outdoor entrance or exit.
georgestolz said:That's goofy. So, I'm guessing that these are only installed where you can get into the house through the cellar? So this is only an exit to the house? :?:
dlhoule said:infinity said:I would disagree that you can enter a Bilco door. These doors are designed to be locked with a bolt style lock on the inside only. They can not be opened from the outside.
In terms of a switch being required; does this mean if I have a dead bolt on some other door I am not required to have a switch? :twisted:
210.70(A)(3) Storage or Equipment Spaces. For attics, underfloor spaces, utility rooms, and basements, at least one lighting outlet containing a switch or controlled by a wall switch shall be installed where these spaces are used for storage or contain equipment requiring servicing. At least one point of control shall be at the usual point of entry to these spaces. The lighting outlet shall be provided at or near the equipment requiring servicing.