Lighting

Status
Not open for further replies.

sharan

Senior Member
This is for a Warehouse aisles application, using T5HO fixtures. Can I use 30 amp branch circuits (to reduce number of circuits and panels) and 20 amp outlets in the ceiling? Fixture wiring to the outlet to be #14 (cord and plug).
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't think you can do this although I don't know what a TSHO fixture is. I am assuming it is a HO fluorescent fixture.. Read art. 210.21(B)(2) & (B)(3)
 
sharan said:
This is for a Warehouse aisles application, using T5HO fixtures. Can I use 30 amp branch circuits (to reduce number of circuits and panels) and 20 amp outlets in the ceiling? Fixture wiring to the outlet to be #14 (cord and plug).

I believe that you can install it as you propose and even 15A receptacles would be fine. Since you have not specified the size(VA) or the operating voltage of the fixtures, I presume you intend to use 1 fixture per receptacle. I can't think of any fixture/ballast combinations that would even come close to the receptacle rating. Standard fixtures would be within the rating of the receptacle. Read 210, 220, 240 carefuly. You will need a minimum #10AWG but don't forget about voltage drop.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
weressl said:
Seems to me 240.5(B)(2) addresses the issue.
It seems to me that the use of receptacles, even way above the floor, means that section does not apply here.
 
LarryFine said:
It seems to me that the use of receptacles, even way above the floor, means that section does not apply here.

In the handbook, the interpretation seem to cover this specific installation method. It should be acceptable when the supplied cord is installed by the manufacturer, especially since the load is known, dedicated and limited.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Why are we talking about receptacles? The question has to do with lighting outlets, not receptacle outlets.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
charlie b said:
Why are we talking about receptacles? The question has to do with lighting outlets, not receptacle outlets.

What is a 20 amp outlet on a 30 amp circuit? Sounds like a receptacle to me.

and 20 amp outlets in the ceiling?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
infinity said:
What is a 20 amp outlet on a 30 amp circuit? Sounds like a receptacle to me.
Sounds like a lighting outlet to me. Sharan, can you clarify your question?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
charlie b said:
Sounds like a lighting outlet to me. Sharan, can you clarify your question?
'Twas clear to me: 30a breaker and #10 wire (I hope!) supplying 20a receptacles (why not 15a then?), and #14 cords with plugs on the luminaires.
 

haskindm

Senior Member
Location
Maryland
Lighting outlet, receptacle? Who cares?
Bottom line is we are supplying LIGHTING FIXTURES, through whatever method. Since lighting fixtures (luminaires) include LAMPHOLDERS, look at 210.21(A) which requires that lampholders installed on a 30-amp circuit must be the heavy duty type. Since there is no such thing as a heavy-duty fluorescent lampholder, you may NOT install them on a 30-amp circuit. There is no way that you can install fluorescent lights on a 30-amp circuit and comply with the NEC.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Remember the theory that the NEC stops at the receptacle. A receptacle is not a lampholder, heavy-duty or otherwise, and plugging a luminarire, heavy-duty or not, into one does not change that.
 

haskindm

Senior Member
Location
Maryland
The NEC no longer stops at the receptacle, otherwise how could the NEC require vending machines have built-in GFCI protection? But that is another (and rather sore) subject. If the OP is contemplating installing 20-amp receptacles on a 30-amp circuit; 210.24 prohibits this if it is a multi-outlet circuit and 210.21(B)(1) prohibits it if it is a single outlet circuit. If he wants to install 30-amp receptacles and plug lights into them, that gets into a gray area. As you say, in general (with exceptions) the NEC stops at the receptacle. If we know the receptacle is for luminaires, do we have a responsibility to make sure that the provisions of the NEC are met? This may be a loophole, but not one that I would be comfortable with. I can see how it could be justified...
 

brantmacga

Señor Member
Location
Georgia
Occupation
Former Child
weressl said:
Seems to me 240.5(B)(2) addresses the issue.

That's dealing w/ flexible cord taps, not cord-and-plug connections. This code does not apply to the proposed installation.
 

iwire

Moderator
Staff member
Location
Massachusetts
It looks like 210.21(B)(3) Exception 2 and 410.30(C)(2) will allow the 30 amp circuit to supply 15 or 20 amp receptacles that supply HID fixtures. (2005 NEC)
 

iwire

Moderator
Staff member
Location
Massachusetts
charlie b said:
Why are we talking about receptacles? The question has to do with lighting outlets, not receptacle outlets.

Many times high bay HID fixtures are hung from hooks then cord and plug connected. When the fixture needs servicing you can quickly exchange it with a working fixture then repair the bad fixture on a bench instead of above peoples head. :smile:
 