Chris why would this matter?Welcome to the forum.
Is this a dwelling unit or commercial?
Chris
can i take power from a hallway lighting circuit to feed a bathroom or bathrooms vanity lights
Chris why would this matter?
dwelling unit: you can feed bath lights, but not bath receptacle outlets.
non-dwelling unit: feed either
which is probably 100% correct... I just felt his question was worded in "code"... could be read either wayOf course. I wasn't thinking of the receptacle. I was thinking lighting.
dwelling unit: you can feed bath lights, but not bath receptacle outlets.
non-dwelling unit: feed either
Augie where is it mention in the code about non-dwelling. I agree with you but I want to mark my book. I am reading in 210 but I don't see it. Its probably right in front my eyes but I don't see it. Thanks
gus
210.11(C)(3) Dwelling Units.
Bathroom Branch Circuits. In addition to the number of branch circuits required by other parts of this section, at least one 20-ampere branch circuit shall be provided to supply bathroom receptacle outlet(s). Such circuits shall have no other outlets.
Exception: Where the 20-ampere circuit supplies a single bathroom, outlets for other equipment within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)(1) and (A)(2).
FPN: See Examples D1(a), D1(b), D2(b), and D4(a) in Annex D.
Infinity, I read that. 210.11C Dwelling units but what about non-dwelling. You mean if it doesn't mention it in dwelling units then it is Ok to do it in non-dwelling.
Infinity, I read that. 210.11C Dwelling units but what about non-dwelling. You mean if it doesn't mention it in dwelling units then it is Ok to do it in non-dwelling.