ronald3

New member
What is the ruling on fluorescent lighting in a machine shop; strip lights, covered lights, height limitations, etc.? I can't locate any specifics in the code book.
 

ldonihoo

New member
Re: Lighting

it has to have 15 caddle power in walk ways and 65 caddle power in work areas this is osha i put 400 watt highbays which gave my guys 200 250 in the work areas but you must have emer lighting for power loss
 

jerryb

Senior Member
Re: Lighting

Too bad we don't measure light in caddle (spelled candle) power. The correct term would be "footcandles". If someone puts 200 to 250 in a work space then the workers will go blind from the glare.
 

jtb

Senior Member
Location
Pennsylvania
Re: Lighting

Cattle power. More beef per watt. :D

Here is a good ref.

http://www.guth.com/products/pdf/t13-t19.pdf

Oh yeah, forgot about flicker!
If you have rotating machines, standard magnetic ballasts can sometimes make them look still if flickering at near the same frequency. HID also.

Solution: electronic ballasts (higher frequency flicker) or alternate phases of adjacent lights.

HID can be ordered with restrike quartz lamp for emergency lighting.

I guess you need more than light level after reading your post again. I think Osha or NFPA 101 is what you are looking for.

Sorry for the wind above... :roll: