What is a better air terminal: Flathead or a pointed tip?
Thanks for your help.
Thanks for your help.
Brian,And MOST importantly, stay away from any and all ESE, radioactive, or other non-conventional products found on the market today.
Brian,
Do you have any reasons for this statement?
Not that Brian needs any tactical air support, but ..... from a design professional standpoint, if you need to go in front of a judge and they ask you why you used a lightning protection method not documented by a nationally recognized organization like NFPA, especially in their lightning standard 780, the stuff will hit the fan.Do you have any reasons for this statement?
and as a side note, I like Franklin's theories better anyway.![]()
Yes, research.
A good start would be here:
http://www.lightningsafety.com/nlsi_lhm.html
All the papers in Section 5.4.1 - 5.4.14 provide a good basis of information and research on the subject.
There are MANY, MANY, more...
Court decisions have very little to do with science, just that his 'expert' has a bigger one than the other's 'expert'.
This report concerns damage from a lightning strike to the Marriott Hotel in Marco Island, Florida, which occurred on August 23, 2010.
The strike sent a bunch of clay tiles crashing to the ground in an area near a swimming pool. The fallen tiles crushed a table, bounced around and broke a window. There was also electrical damage. Luckily, no one was injured. The damage area was on the southwest corner of the building.
The structure previously had a conventional lps that was replaced with a "Preventor" ESE device during renovations several years ago. The Preventor ESE system had 2 down leads. The distance from the ESE rod to the damaged location was about 204' from the rod to the rear area of the building where the damage occurred. The rod was 94' to the front of the building.
Four photos of the incident are attached. These show location of the struck corner of the building, two photos of the ESE device and its location, and the damage to the roof.
Abdul Mousa, Ph.D., P. Eng., Fellow IEEE
Lightning protection consultant
Vancouver, Canada