spectra05
Member
- Location
- Piedmont, NC
i m trying to put a lightning arrestor on a main panel and i want to attach it to the main CB to protect the entire house if lightning hit from the supply side of the panel. An inspector friend of mine says i cant and is quoting 280.22, saying that because the service to a single family dwelling is less than 1000v. to me that seems like it is saying what size conductors when on the load side and there is no usses permitted or not permitted like there is for TVSS's.But i want to say it ok because of 230.82 (4) which says only the following equipment shall be permitted to be connected to the supply side of the service disconecting means. then part 4 states instrument transformers, impeadeance shunts, load management devices, and arrestors. this is from NEC 2005 edition. any help would be great.