Re: Lightning & conductor impedance
Don, I design and write lightning, grounding, and protection engineering practices for telephone companies. If you want to stick a label on it its called a Power Protection Engineer, or Central Office Power Engineer.
You have a point in one since, but might be overlooking some mechanics. You are correct, the impedance of a conductor of say 10 feet does exhibits an impedance of around 1000 ohm?s, the size of the conductor is insignificant. When you talk about a 5-ohm GES, you are taking reference at say136 hertz, which has nothing to do with lightning frequencies. So you are trying to add 1K-ohm to 5 and come out with 1K, doesn?t work that way. You are trying to add apples to oranges.
OK, enough confusion. When I specify say a 5-ohm system, I want a lot of copper in the ground. The reason is ground saturation and step potential. I want my site to be surrounded by a ring with radials extending away from critical areas. The large amount of copper in the ground gives it the ability to discharge lightning quickly without saturation and minimizes step potential differences to acceptable levels. A single or two-rod system cannot do that. If it were not specified, you can imagine what you would get.