Member
- Location
- south missouri
Engineer wants aluminum cupola, on top of new building, "grounded to provide lightning protection." During phone conversation, he was concerned about a direct lightning strike to this piece of aluminum equipment on roof. Initially, this bare 3/0 copper conductor was supposed to be ran in pvc conduit, completely independent of all other conductors, and ran to 3 seperate ground rods, then bonded to the building steel, which is being used as an electrode.
Electrical contractor can not route conductor independently, due to building already being completed. So electrician's solution was to run conductor in existing, interior metal raceway, through service equipment pullbox, then through service CT metering cabinet, then finally down to ground rods. He commented it was his only option to go from point A to point B.
#1) So what does this 3/0 copper conductor qualify as?? Not a GEC, but it's connected to grounding electrode system.
#2) Isn't routed through service raceways and CT metering equipment the last place you would want a "lightning conductor"??
Electrical contractor can not route conductor independently, due to building already being completed. So electrician's solution was to run conductor in existing, interior metal raceway, through service equipment pullbox, then through service CT metering cabinet, then finally down to ground rods. He commented it was his only option to go from point A to point B.
#1) So what does this 3/0 copper conductor qualify as?? Not a GEC, but it's connected to grounding electrode system.
#2) Isn't routed through service raceways and CT metering equipment the last place you would want a "lightning conductor"??