Lightning Protection - Air Terminal

Status
Not open for further replies.

anbm

Senior Member
To follow up previous post, I also saw a note from Lightning protection drawing indicates " where the metal bodies 3/16" or thicker do not require air terminal ", I am doing the research on nfpa-780 to see where does this rule comes from. Any comments will be appreciated. Thanks!
 
You will find it in NFPA 780.
The concept is that 3/16" steel will act as a terminal. It needs to be bonded like any other air terminal.

4.8.8.1
Chimneys or vents with a metal thickness of 4.8 mm
(3⁄16 in.) or more shall require only a connection to the lightning

protection system.

6.10.1
Heavy-duty metal stacks having a metal thickness of
4.8 mm (3⁄16 in.) or greater shall not require air terminals or

down conductors.

7.1.2.1
Metallic structures that are electrically continuous;
tightly sealed to prevent the escape of liquids, vapors, or gases;
and of 4.8mm(3⁄16 in.) thickness or greater to withstand direct
strikes in accordance with 7.3.2 shall be considered to be inherently

self-protecting.


 