Lightning Protection and Ground Rods

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
The IEC Technical Committee 81 responsible for lightning protection of structures has published hypothetical scenarios for the division of lightning current for structures struck by lightning using both lightning protection, surge protection devices, and employing proper NEC required service grounding. In their report, current distribution through all the connected components of the grounding system should follow Kirchhoff's current law. The NFPA 780 and IEC 81 are based on this principle.

For example, assume two round rods installed roughly 10' apart. One is connected to the LPS the other is the grounding electrode for the building service. Both rods are bonded together. At the service, a SPD is installed. Under the IEC assumption, if 100kA lightning current is injected into the LPS, 50kA would flow to ground in LPS ground rod, 50kA from the LPS rod to the service rod, 25kA to ground through the service rod, 25kA into the house via the GEC, and then 12.5 split between the SPD and the service neutral. Obviously, there would be some variances depending on the true resistances and impedance of the current paths.

In order to test this hypothesis, the above configuration was established at a test house at the International Center for Lightning Research and Testing at Camp Blanding here in Florida. Three tests were performed and the results published in the IEEE Transactions on Power Delivery, Vol. 17, No. 2.

In each of the three tests, the configuration and connections remained the same. Only the ground resistance of each rod was altered for each test. On the third test, the SPD was removed. Attached to the LPI ground rod was a 60' braided tether to a rocket which initiated lightning from natural thunderclouds in order to inject the lighting currents directly to the LPS. The structure was connected to a service entrance form the secondary of a transformer around 150' away but left unenergized.

In test #1, the grounding resistance of each rod was quite high ranging from about 500-ohms to over 1,500 ohms. In test #2 and #3 the ground resistance was reduce to under 100-ohms.

What resulted in quite interesting and unexpected. The ground rods appeared to filter out the higher frequency components of the lightning current, allowing the lower frequency components to enter the house's electrical system. This means that ground rods (electrodes) actually exhibit a capacitive behavior rather than the expected resistive behavior as long assumed. The peak current that entered the home exceeded 80% of the total injected lightning current. There were almost no differences in the measured currents at all points even after the ground resistance was reduced by over 1,000-ohms. Upon excavation of the service cable supplying the structure, 40 pinholes were found in the neutral insulation. On test #3 after the removal of the SPD, significant damage of the service equipment resulted that was not observed after the first 2 tests.

The bottom line is that based on this set of tests a few assumptions can be made:

1. LPS don't work.
2. SPD's do work.
3. Ground rods and other electrodes are useless for lightning currents.
4. The NEC grounding requirements and the NFPA 780 is likely to be ineffective and unfounded.
 
By the way, The IEC 61024-1(4) does not contain any requirement for the value of grounding resistance of an ordinary building in which level III/IV protection is used. This is the level of protection generally used on 1&2 family dwellings. This is just more evidence that the 25-ohm requirement in the NEC has no merit or justification.
 
About what I figured...

About what I figured...

You know Brian, I'm not surprised at all. Can you tell me how I can get a copy of the reports you base your summary on? Since I live in Florida (near Gainsville) do you think that I could attend any future testing? :roll:
 
Because of the on going debate between Franklin's system and the other systems @ NFPA, the first question I'd like to ask is who funds the International Center for Lightning Research and Testing?
I'm curious how much debate occurred at the IEEE conference that it was presented in prior to its publication in IEEE Transactions on Power Delivery.
I was just at an IEEE conference earlier this week in Michigan, where a controversial topic (stray current in agricultural building) was beaten up. But other controversial topics, had very little debate because of low attendance at that particular presentation. It depends on the interests of those that attend.
 
bphgravity said:
This is just more evidence that the 25-ohm requirement in the NEC has no merit or justification.
Bryan, I don't think the 25-ohm requirement has anything to do with lightning.
 
Bryan, I think it is only fair to point out the test are inconclusive as the report itself points out in the Summary and Recomendations. They specifically state the results should change if the test are conducted in something other than non-conductive sandy soils.
 
Thanks for your comment Dereck, and I agree. However this is only one of dozens of reports that are indicating the same results.

There is way more evidence that grounding is less functional from a performance standpoint than there is evidence the afci's are useful, yet look how things are changing in the NEC.

The CMP members seem to be quick on accepting new products with no historical performance review yet allow long mis-applied code sections to stay in with any change in nearly 100 years.
 
try reading: REPORT OF THE COMMITTEE ON ATMOSPHERIC AND SPACE ELECTRICITY OF THE AMERICAN GEOPHYSICAL UNION ON THE SCIENTIFIC BASIS FOR TRADITIONAL LIGHTNING PROTECTION SYSTEMS
14 pages in adobe reader, long but very enlightening
 
less than 1 ohm impedance for communication tower

less than 1 ohm impedance for communication tower

hi im ganesh here,

im having trouble figuring out the most appropriate way to lower the earth impedance less than 1 ohm for communication tower. do you have any better idea to reduce it apart from consuming large area with so many electrodes at the site. :?
 
There are several methods and products available on the market that can provide very low initial ground resistance. The most common is soil treatment materials or chemical rods. The problem is that any method degrades over time depending on conditions. Most methods will require periodic testing to ensure the product or method is still performing to its intended level.
 
Re: less than 1 ohm impedance for communication tower

Re: less than 1 ohm impedance for communication tower

ganesah said:
im having trouble figuring out the most appropriate way to lower the earth impedance less than 1 ohm for communication tower. do you have any better idea to reduce it apart from consuming large area with so many electrodes at the site. :?

I do this for a living, and the answer is no. Each site is unique, requires soil test studies, and individual techniques.

To be honest and let you in on a secret, the impedance does not matter. Now days I just use a cookie cutter design and what ever impedance I get is what the spec is.
 
Thank you very much for your reply.

Sir I still have few questions running through my head.

If you do not mind please brief me on what is cookie cutter design is about?

to do the soil testing in communication tower site, how deep and wide should the soil be taken for testing (if there are no standard measurement than what do you recommend).?

Sir, i have gone through a book entitled 'Designing For A Low Resistance Earth Interface (Grounding)' by Roy B. Carpenter,Jr. and Joseph A.Lanzoni.
Many approaches to obtain desired result were brought forward together with a formula. One of them is as follows:

Replacing soil in the Interfacing Hemisphere (IH) (required amount of soil surrounding electrode needed to complete the electrical connection )

 Replace only the part of the soil that gives the most effect on the grounding resistance not the whole IH which is called Critical Cylinder.
 Use the lowest resistivity soil available.
 Next step, select proper backfill or soil to replace it within the Crytical Cylinder.
 Again if one rod doesn?t achieve the desired goal, multiple rods must be considered.

What do you think with the method?

when dealing with the electrodes only,
from your point of view, what should be the distance between each rod and how many of them needed to get lower impedance?

And what do you think the best grounding electrode length for a communication tower?
 
The IEC Technical Committee 81 responsible for lightning protection of structures has published hypothetical scenarios for the division of lightning current for structures struck by lightning using both lightning protection, surge protection devices, and employing proper NEC required service grounding. In their report, current distribution through all the connected components of the grounding system should follow Kirchhoff's current law. The NFPA 780 and IEC 81 are based on this principle.

For example, assume two round rods installed roughly 10' apart. One is connected to the LPS the other is the grounding electrode for the building service. Both rods are bonded together. At the service, a SPD is installed. Under the IEC assumption, if 100kA lightning current is injected into the LPS, 50kA would flow to ground in LPS ground rod, 50kA from the LPS rod to the service rod, 25kA to ground through the service rod, 25kA into the house via the GEC, and then 12.5 split between the SPD and the service neutral. Obviously, there would be some variances depending on the true resistances and impedance of the current paths.

In order to test this hypothesis, the above configuration was established at a test house at the International Center for Lightning Research and Testing at Camp Blanding here in Florida. Three tests were performed and the results published in the IEEE Transactions on Power Delivery, Vol. 17, No. 2.

In each of the three tests, the configuration and connections remained the same. Only the ground resistance of each rod was altered for each test. On the third test, the SPD was removed. Attached to the LPI ground rod was a 60' braided tether to a rocket which initiated lightning from natural thunderclouds in order to inject the lighting currents directly to the LPS. The structure was connected to a service entrance form the secondary of a transformer around 150' away but left unenergized.

In test #1, the grounding resistance of each rod was quite high ranging from about 500-ohms to over 1,500 ohms. In test #2 and #3 the ground resistance was reduce to under 100-ohms.

What resulted in quite interesting and unexpected. The ground rods appeared to filter out the higher frequency components of the lightning current, allowing the lower frequency components to enter the house's electrical system. This means that ground rods (electrodes) actually exhibit a capacitive behavior rather than the expected resistive behavior as long assumed. The peak current that entered the home exceeded 80% of the total injected lightning current. There were almost no differences in the measured currents at all points even after the ground resistance was reduced by over 1,000-ohms. Upon excavation of the service cable supplying the structure, 40 pinholes were found in the neutral insulation. On test #3 after the removal of the SPD, significant damage of the service equipment resulted that was not observed after the first 2 tests.

The bottom line is that based on this set of tests a few assumptions can be made:

1. LPS don't work.
2. SPD's do work.
3. Ground rods and other electrodes are useless for lightning currents.
4. The NEC grounding requirements and the NFPA 780 is likely to be ineffective and unfouded.



Great work Bryan in locating and posting these results. I think I will have a bunch of copies made, laminated, and attach one to each ground rod I have to put in. Changing the mindset, one ground rod at a time........ I wonder what the results would have been if a CEE was also present. I personally doubt the effectiveness of this method also. (especially slab on grade, with plastic film between earth and concrete.)
 