If you have multiple antennas (with attached cables) installed on the edge of roofline that needs a lightning protection system, how do you meet the requirements in NEC 820.44 (E)(3) and NEC 830.44(G)(3) while meeting the requirement in NFPA 780 section 4.7.2.1? The antennas can not be relocated. The NEC requirements both begin with "Where practicable", making it a suggestion, not a requirement?
Side flash distance calculated from NFPA 780 section 7.6.5.2 is about 1.5 feet. So I should be ok if we make the lightning conductor distance from the roofline a minimum of 1.5 feet and a max of 2 feet, right?
I've been told that the communications systems are fully protected for surges, etc. NFPA 780 section 4.17 states that the antennas must be connected to the protection system using conductors, but this requirement also seems to conflict with the requirements in the above stated NEC codes. Thoughts? The antennas are taller than any air terminals would be. Any other considerations for the antennas and the cables that are attached to them?
There is metal conduit installed on the exterior of the building or lighting circuits that originate inside the building. Do I tie these to the protection system, or would that cause problems inside?
I know there are a lot of questions here. Thanks for your help!
Side flash distance calculated from NFPA 780 section 7.6.5.2 is about 1.5 feet. So I should be ok if we make the lightning conductor distance from the roofline a minimum of 1.5 feet and a max of 2 feet, right?
I've been told that the communications systems are fully protected for surges, etc. NFPA 780 section 4.17 states that the antennas must be connected to the protection system using conductors, but this requirement also seems to conflict with the requirements in the above stated NEC codes. Thoughts? The antennas are taller than any air terminals would be. Any other considerations for the antennas and the cables that are attached to them?