Lightning Protection System Bonding

Status
Not open for further replies.

masterelect1

Senior Member
Location
Baltimore
The IEEE standard requires bonding grounded equipment in close proximity to the LPS cable going to earth ground. The installer has bonded his LPS system cable to a 1 1/2" black iron pipe which is being used to carry Natural Gas to rooftop humidifiers. This bonding to a natural gas line seems to be a hazardous situation.

Comments ??

Thanks,
John
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't believe it will hurt to bond the gas line. Where the flexible gas lines are used we are now required by the manufacturers to bond the pipes-- known as CSST piping.

The gas companies however do not like it but they usually have a dielectric fitting at their meter.
 