For all you guys who see these systems:
The building is a 20 story office building. There are air terminals on the roof all connected together. No problem so far.
The air terminals then use building steel as a down conductor. Is this standard practice?
At the column pads, a conductor is cadwelded to the base of the steel column and taken out to a bunch of ground rods.
I see maybe a conflict with 250.60, since we are using the building steel as a down conductor. You can't use down conductors for lieu of an electrode. So then I could not ground a XFMR to building steel.
The plans are stamped by a master lightning guy (official title escapes me) whose company provides a UL certification on the system.
Any thoughts?? Seemed strange to me, but then I work in my attic in the summer.
The building is a 20 story office building. There are air terminals on the roof all connected together. No problem so far.
The air terminals then use building steel as a down conductor. Is this standard practice?
At the column pads, a conductor is cadwelded to the base of the steel column and taken out to a bunch of ground rods.
I see maybe a conflict with 250.60, since we are using the building steel as a down conductor. You can't use down conductors for lieu of an electrode. So then I could not ground a XFMR to building steel.
The plans are stamped by a master lightning guy (official title escapes me) whose company provides a UL certification on the system.
Any thoughts?? Seemed strange to me, but then I work in my attic in the summer.