When I wired fuel systems we were required to install (2) ground rods at opposite sides of the tanks and bond the tank to the ground rod. The theory as I remember it was the lighting was not going to damage the tank but they wanted the lightning to drain. It was not an NEC requirement at the time, but some NFPA document (that I don't remember).
NFPA 780 Chapter 7 Protection for Structures Containing Flammable Vapors, Flammable Gases, or Liquids That Can Give Off Flammable Vapors
7.2.2 Inherent Protection. Metallic structures that are electrically continuous; tightly sealed to prevent the escape of liquids, vapors, or gases; and of 3/16in. (4.8mm) thickness or greater to withstand direct strikes shall be considered to be inherently self-protecting.
7.3.7 Grounding.
7.3.7.1 A ground ring electrode or ground loop conductor supplemented by grounding electrodes as identified in 4.13.2 through 4.13.7 shall be provided for structures containing flammable vapors, flammable gases, or liquids that can give off flammable vapors.
7.3.7.2 A metal tank shall be grounded by one of the following methods:
(1) A tank shall be connected without insulated joints to a grounded metallic piping system.
(2) A vertical cylindrical tank shall rest on earth or concrete and shall be at least 20ft. (6m) in diameter, or shall rest on bituminous pavement and shall be at least 50ft. (15m) in diameter.
(3) A tank shall be grounded through a minimum of two grounding electrodes, as described in section 4.13, at maximum 100ft. (30m) intervals along the perimeter of the tank.
(4) A tank installation using an insulating membrane beneath for environmental or other reasons shall be grounded as in 7.3.7.2(3).