Hi,
I perform a lightning risk assessment about once a year using the NFPA 780 calc (annex L). It involves comparing the risk of lightning to the tolerable frequency. The problem is, every building I ever calc says it needs a lightning protection system (LPS). Literally a 50x50x15 office building gives a positive result. I am in the northeast and just don't believe that every building needs a LPS. Why haven't they all burned to the ground? I am having trouble using the calc since it seems to biased and never gives me a negative result. I checked the math twice and still have this issue.
Anyone run into the same issue or have a better calc they use?
Math below:
Btw, very similar to the calc here: http://alltecglobal.com/resources/lightning-risk-assessment
I perform a lightning risk assessment about once a year using the NFPA 780 calc (annex L). It involves comparing the risk of lightning to the tolerable frequency. The problem is, every building I ever calc says it needs a lightning protection system (LPS). Literally a 50x50x15 office building gives a positive result. I am in the northeast and just don't believe that every building needs a LPS. Why haven't they all burned to the ground? I am having trouble using the calc since it seems to biased and never gives me a negative result. I checked the math twice and still have this issue.
Anyone run into the same issue or have a better calc they use?
Math below:
Building dimensions: | ||
L (m) | 16 | |
W (m) | 16 | |
H (m) | 5 | |
Ae | 1923 | |
Ng (flash density) | 2 | |
Ae | 1923 | |
C1 | 0.5 | |
Nd (lightning strike frequency) | 0.00192262 | |
C2 | 1 | |
C3 | 1 | |
C4 | 1 | |
C5 | 1 | |
C | 1 | |
Nc (tolerable lightning frequency) | 0.00150 | |
Nd | 0.00192262 | |
Nc | 0.0015 | |
Results: | ||
Is Nd<=Nc | no | |
| ||
if Nd>Nc | yes
|